paulz
Member
|
# Posted: 12 Jul 2021 10:46am
Reply
Man likes his coffee..
When the SCC shows 14+ volts, which mine rarely does, it's bulk charging? Was there some usage that caused the need for bulk charging?
I programmed my Epever for LFP (has no pre-programmed setting) according to the values Battleborn suggests:
Over Voltage Disconnect 14.7 V
Charging Limit Voltage 14.6 V
Over Voltage Reconnect 14.6 V
Equalize Charging Voltage shut off or 14.4 V
Boost Charging Voltage 14.6 V
Float Charging Voltage 13.6 V
Boost Reconnect 13.3 V
Low Voltage Reconnect 10
Under Voltage Warning Reconnect Voltage 11.5
Under Voltage Warning 11.5
Low Voltage Disconnect 11.0
Discharging Limit Voltage 10.5
Equalize Duration 0 or set as low as possible
Boost Duration 180 minutes
|
|
gcrank1
Member
|
# Posted: 12 Jul 2021 02:15pm
Reply
Those settings may well come in handy for me as I transition to LFP! My old (Mirro-Ware?) 30 cup perc is our water heater; 1000w @ 115vac. It runs fine off the Lil' Champ 1600/2000 inv/gen but no way Im going to try to set up for 90ish w off the 12v bat-bank and inverter. And no need to with a one-pull little genny for a short run. Fwiw, Ive watched the read-out on my scc, when the bat-bank is full and setting on 'charge current to bat', go up from 'x amps' at maintenance to 'whatever more' the device is I turn on. Kinda handy to see what something is actually using off the array. I have been thinking of trying to use my toaster off the inv. as a load tester for each battery; ever try anything like that?
|
|
paulz
Member
|
# Posted: 12 Jul 2021 02:37pm
Reply
I have not. Like you, my electrical needs have been small, LEDs, phone chargers, laptops.. I just recently added a small PSW 1500 inverter to power a ceiling fan, and have started to play around with AC things, vacuum cleaner, tool chargers. Again a slippery slope, wife would love a big screen TV.
Here is the link to the Battleborn page with the LFP specs.
https://battlebornbatteries.com/setting-up-the-epever-solar-controller/
|
|
paulz
Member
|
# Posted: 25 Jul 2021 01:28pm
Reply
Tell me again why I can't jumper and charge my dump truck battery off the cabin's 12v, LFP solar battery bank? Seems to me it wouldn't be any different than any other system draw.
|
|
ICC
Member
|
# Posted: 25 Jul 2021 06:29pm
Reply
Are the charge requirements and limits betwwen the LFP and lead-acid identical?
An LFP battery has a lower internal resistance than lead-acid. The LFP will probably reach full charge before the lead-acid battery. The CC will still be trying to send the lead-acid battery current that the LFP does not need. The CC cannot just send power to the battery with the lower state of charge. The charge current goes to everything that is connected. Does the LFP have a BMS that can deal with the voltage/current the lead-acid battery still needs?
All the dame caveats that apply to all parallel connected batteries apply, and are complicated by the different chemistries and their different limits.
|
|
gcrank1
Member
|
# Posted: 25 Jul 2021 06:41pm
Reply
Isnt the simple solution to just plug a typical fla battery charger into the inverter running off the lfp bank? Yeah, inefficient dc to ac to dc, I get it. But so what, its all running off your 'free' solar anyway.
|
|
paulz
Member
|
# Posted: 25 Jul 2021 06:46pm
Reply
Sounds complicated, I'll just use a charger off the inverter, as I do with the tool batteries. Thanks.
|
|
paulz
Member
|
# Posted: 4 Aug 2021 04:16pm
Reply
Renogy... can't say I wasn't warned.
My first CC fried the mosfets. I did exceed the 100v pv voltage by a bit, but it was supposed to shut itself off. Oh well. I replace it with an Epever, been fine since.
I bought another one, why I don't remember, that's been sitting on a shelf. I decided to hook it up, 20 amp, to a couple of 100w, 30v, 6a panels in series, just to charge car batteries. Put a battery with about 12.4 on it one day, showed it was charging it, went back to the city for a couple of days. Got back, CC showed error E01, insufficient battery voltage. Sure enough, down to 11v.
Hmmm, maybe the battery is toast says I. So I put a different battery on, and put the battery on another charger. Got back here today, another E01 error and dead battery. First battery, on the other charger is fully charged.
Somehow this Renogy is draining my batteries. No load of course. I just hope it didn't do too much damage.
|
|
Steve_S
Member
|
# Posted: 4 Aug 2021 04:44pm
Reply
I'm sorry to hear that Paul. Not sure how to help you troubleshoot that. The EPEver products are very good "value+" gear. I would first suggest putting the batteries on a proper Bech Power supply with CC/CV and run then down to 10% and Max Charge Amp to full at least twice, which often will "kick" them. IF Lead Acid, double check fluid levels 1st! Sorry I forget if you are using only LFP or a Combo of chemistries now, your stuff has evolved a lot.
I guess once I heal up good enough, and finish the "Toolshed" project and its own Solar System, I'll have to post that up here & @ DIY as well for folks. It's Different, using a Midnite Solar KID MPPT SCC and a few other cool goodies. An alternate kind of system. Sadly, I've spent more time in hospital this past 45 days then I have in the past 6 years.
|
|
paulz
Member
|
# Posted: 4 Aug 2021 04:53pm - Edited by: paulz
Reply
Sorry to hear about the hospital time Steve. I've been fortunate to having only spent a few hospital days so far in my life, but enough to know it's not fun.
I should clarify the CC giving me the E01s is another Renogy, not the Epevers I use at both cabin (LFP) and shop (FLA). It's just a spare I had kicking around but was new in the box. I'm just trying to charge the batteries for the trucks and tractors with it, no load. I know the CCs take some power to run but shouldn't kill car batteries. The first one, that I recharged on another charger, I put it in a tractor and it cranked right over so it couldn't be in that bad a shape
|
|
gcrank1
Member
|
# Posted: 4 Aug 2021 09:51pm
Reply
I expect that discharge took some life out of those bats but no way to quantify that; they will live until they die. Do those panels have anti-backflow diode?; ie, maybe its not the scc.
|
|
paulz
Member
|
# Posted: 4 Aug 2021 09:58pm
Reply
I've never seen a diode on any panel, where to look?
|
|
gcrank1
Member
|
# Posted: 4 Aug 2021 11:00pm
Reply
Read about 'em, never seen one; my impression has been they reside in the 'box' on the back of the panel. Iirc, one way to tell if you dont have such or it is 'blown' is if a battery goes dead overnight; ie, the juice gets sucked back out if the panels arent pumping it 'in'. Im sure somebody else can clarify this for us.
|
|
paulz
Member
|
# Posted: 10 Aug 2021 10:36am
Reply
Quoting: gcrank1 Im sure somebody else can clarify this for us.
No update from the resident pros.. I looked at the two panels yesterday, couldn't see a way to open the little box.
Seems odd though that the CC would allow the juice to get sucked back out.
|
|
Steve_S
Member
|
# Posted: 10 Aug 2021 12:17pm
Reply
The diode is in that little black box, It cannot be removed from panel nor can it be opened. Well, you can try but failure = junked panel. Some have managed to repair them but not many and I believe it has a lot to do with brands because those housing vary a fair bit.
|
|
gcrank1
Member
|
# Posted: 10 Aug 2021 12:48pm
Reply
Steve, can an add-on diode be wired in the + or - leads out of the sealed box?
|
|
Steve_S
Member
|
# Posted: 10 Aug 2021 01:17pm
Reply
Apparently, it is possible. There are several Youtube Vids and also threads on DIYSolarForum.
|
|
paulz
Member
|
# Posted: 12 Aug 2021 05:12pm - Edited by: paulz
Reply
Was walking by today and flipped one over. Covers pop right off,has diodes. Now if someone can tell me how to test with a VOA meter...
|
|
paulz
Member
|
# Posted: 15 Aug 2021 07:49pm
Reply
So I tested these diodes today. My VOM has a diode setting, the triangle icon. For some reason these two panels have two diodes each, connected to a center tap that isn't used. See photo above.
When I tested them independently I got the correct results; .5v in one direction and open in the other. But when I test both together (at the two end terminals) I got open in both direction for some reason.
I'm going to hook an ammeter in series next, along with the CC and see what it says.
|
|
paulz
Member
|
# Posted: 13 Sep 2021 10:58am - Edited by: paulz
Reply
Ha, so getting back to post #1 on this thread..
I finally put in use the array I bought to start my solar, it had been sitting stagnant as not a week later I was given the 30 panels I've been using. I have this 900w array on the shop roof now (the blue tarp is covering the PVC membrane until I find something to put over it), freeing up 12 panels I can now use up at the cabin.
It's 6 series panels x 2, puts out a bit over 100v, feeding the 150v SCC. Less juice than the other panels but I'm only working down there every few days. We'll see how it goes over winter.
I mounted casters to it, I can wheel it around for max charging but have to walk up onto the roof. Maybe with some ropes and pulleys.. Also need to lash it down if it ever gets windy here.
|
|
gcrank1
Member
|
# Posted: 13 Sep 2021 03:32pm
Reply
Ropes and pulleys, I love it! My wife makes fun of me when I haul out ropes and pulleys......
|
|
paulz
Member
|
# Posted: 13 Sep 2021 09:41pm
Reply
Today I looked at the SCC with the array in the shade like above, about 1 amp charge. Went up there and wheeled it in the sun, 8 amps. Maybe I can leash my dog to it and teach him to keep it in the sun.
I just bought a package of 6 40w 4,500 lumen 4' LED shop lights for 100 bucks on Amazon. Put them up today. Really lights up the shop when all lit but I better take it 1 or 2 at a time where I'm working.
|
|
gcrank1
Member
|
# Posted: 13 Sep 2021 11:44pm
Reply
Ive been replacing my ancient fluorescents with the led shop lights at home, wow, I love em! Light-weight, easy to install, no flicker or fuss. If you can figure a window of time that you would be most likely to be using power and/or needing a recharge and positioning the array for that it might keep up without you moving it around much. Thats why mine is set SE now and I get good am recharging thru 1pm even in light overcast.
|
|
paulz
Member
|
# Posted: 14 Sep 2021 09:59am - Edited by: paulz
Reply
Yeah I replaced the fluorescents in my house garage awhile ago. I bought one at Costco and realized it even has a remote, which I never use, but it turns on automatically when I walk in the garage. I like that, it's above the tool boxes which I often just drop in quickly to grab a tool out of.
There is a big stand of trees blocking the mid-morning southern sun. I get some sun earlier, then around 12-2, then more trees for the remainder.
If I do put the other 10 of my 30 panels up at the cabin I'll have more juice than I need, pretty sure. I have two inverters up there now, one inside and one outside in a box. I may try a 200' 110ac run down to the shop.
|
|
paulz
Member
|
# Posted: 16 Dec 2021 10:22am
Reply
I've been getting decent charging at the cabin since I moved the panels higher up the hill, however I'm getting next to nothing with the array I have down at the shop (first pic in this thread). When I disconnect it from the SCC it reads 100+ volts, connect it and the SCC reads 14v, don't remember the amps but almost nothing.
The odd thing is when first reconnected, the SCC does read some higher voltages and amps, 50 or more and a couple amps, green charge light blinking. A few minutes later it's down to 14 again. Travellerw mentioned some bugs and inconsistency with the Epever Tracers, makes me wonder.
Can I measure the panels for amperage without hooking to the SCC somehow?
|
|
travellerw
Member
|
# Posted: 16 Dec 2021 10:53am
Reply
Quoting: paulz Can I measure the panels for amperage without hooking to the SCC somehow?
For large arrays still wired together, a quick and dirty trick is to hook the array directly to a mostly discharged battery and use a multimeter and clip on DC amp meter to read the watts (V x A). Of course you do it quick and use care as hooking 100V to a 12V battery can cause "issues". DO NOT DO THIS TO A LiFePO4 battery, only FLA and the bigger the bank the better!
A BETTER WAY! Individual panels can be tested using just a multimeter (as long as current doesn't exceed 10A). I will leave 2 videos below and how to test panels and diodes on the panels.
At 100V it would seem that the array is wired in series. Depending on the type of panels (and a bunch of other factors), series wired arrays can perform VERY poor in any shade. I have seen an array completely brought to its knees by just the shadow of a single line (rope). Then you add the poor software in the EPEver and it could be your problem.
Another issue could be a high resistance connection somewhere. MC4 connectors are famous for that. Voltage is good, but once you try pulling any amps things fall down. However, usually the offending connector will get hot. You would be shocked how many good panels get thrown out for poor connections.
If it was me, I would probably rewire that array in a parallel arrangement. At the same time I would redo the connectors.
Here are the mentioned Videos. Diodes https://www.youtube.com/watch?v=tKyOAcplW7g&ab_channel=altEStore
Output test https://www.youtube.com/watch?v=eh6hzMb69gY&ab_channel=altEStore
|
|
paulz
Member
|
# Posted: 16 Dec 2021 02:26pm - Edited by: paulz
Reply
Thanks Trav. Good videos, I love it when ladies talk tech. I would have done more testing this morning but my wife was anxious to get back to urbanville.
This array was my first venture into solar. I had gone to buy an inverter off Craigslist and the guy offered it to me for $300, so I impulse bought it. That same weekend I was bragging about it to friend whose friend bought a house and wanted the solar system gone, 30 panels. So that's what I'm using at the cabin and this array has been mostly sitting.
Anyway this is how it's wired up, 2 strings in parallel, 6 panels per. No MC4, this thing is old, probably predates it. Also might be why it's not putting out.
I should take it apart and maybe spread the panels around in parallel, but it's nicely put together and wired, and it does put out juice when it gets good sun.
Anyway I'll do more testing next trip out. 20211216_0941001.j.jpg
| solar.JPG
| | |
|
|
paulz
Member
|
# Posted: 21 Dec 2021 08:08pm - Edited by: paulz
Reply
Checked this array today. No sunshine. 115 volts but only .16 amps, .08 per string. I disconnected one panel, it was putting out about .012, so with 12 panels the .16 amps. Don't know what should be expected on a cloud covered day, with tree shade to boot. This was with the ammeter connected straight to the panels, no battery.
I noticed this 6/12 volt diagram for the wiring, why would you use one over the other? 20211221_110608_2..jpg
| 20211221_110608_2..jpg
| | |
|
|
travellerw
Member
|
# Posted: 21 Dec 2021 09:34pm
Reply
Only 18W on a cloudy day with the panels not angled perfect.. That is realistic..
The fact that those panels have a 12 and 6 volt config, seem to verify they are pretty old.
Old panels like that usually perform pretty poor in series... but cloudy conditions really kill production anyway!
|
|
paulz
Member
|
# Posted: 21 Dec 2021 09:51pm
Reply
They are Seimens SP75s. I have seen references back to 2008 but they could well be much older. Do you think rewiring to say 4 parallel 3 panel string would do much?
|
|