I'm running off-grid at my cottage (don't have a choice) 5x 50Ah 12v batteries...1000 Watt inverter...and 1x (for now) 60 Watt Solar panel...
I only use to power a maximum of 8x 9 Watt lights and a TV/DVD... I need to consider that I will need in the near future a on-demand pump for water but that's about it!
I just don't want to start a fire!!! My cottage is wired like a real house (120v...) and I plug everything in the inverter... Just want to know if I really need to go to #2 wire size between batteries and between inverter??? Any tips you have would really help!
Everything's been working fine for the past 3 years... There's a daughter now in the picture and safety is #1!
|
|
rayyy
Member
|
# Posted: 15 Feb 2011 04:06pm
Reply
howdy Ouello,Can you be more specific on this pump your gonna get?Also not sure if you mean 8 litebulbs at 9 watts each?I'm also curious if you 60 watt solar charging set up is keeping your 5 batterys charged up?
|
|
MikeOnBike
Member
|
# Posted: 15 Feb 2011 04:52pm - Edited by: MikeOnBike
Reply
Your inverter should be very close to your batteries so the length of #2 shouldn't be a cost issue. How far did you plan to run the #2 wire?
Run the high voltage (120v) line the longer distance as it requires much smaller wire.
|
|
MtnDon
Member
|
# Posted: 15 Feb 2011 05:27pm
Reply
Ditto Mike. The inverter should have had minimum wire sizes for different distances. In my book it is best to use a size larger than their minimum.
#2 wire should carry the expected load out to 12 feet max, more or less. #4 to 8 feet, #6 to 4 feet
|
|
|