# Posted: 6 Jun 2016 06:49pm - Edited by: davestreck
Reply
How close do the specs have to be on two different manufacturers' solar panels to allow you to wire them in parallel to the same charge controller?
I have 2 100w mono panels (1 Renogy, 1 WindyNation) that I'd like to connect to a Morningstar (non-MPPT) cc. The specs are:
Panel 1: Voc 22.1 Isc 5.91 Vmp 18.0 Imp 5.56
Panel 2: Voc 22.5 Isc 5.75 Vmp 18.9 Imp 5.29
Is this close enough to not matter?
[Needless to say, this is part of a 12v system]
|
|
MtnDon
Member
|
# Posted: 6 Jun 2016 07:45pm
Reply
Rule of thumb =
Connecting in series, the Imp should be within 10%, within 5% is better
Connecting in parallel, the Vmp should be within 10%, within 5% is better
|
|
davestreck
Member
|
# Posted: 6 Jun 2016 08:31pm
Reply
18.0/18.9=0.952
Sounds like I'm good to go.
Thanks much!
|
|
|