Author |
Message |
paulz
Member
|
# Posted: 12 Nov 2016 11:15am
Reply
My double wall stove pipe and roof jack. Can I insulate around it with fiberglas? 12' from stove.
|
|
toyota_mdt_tech
Member
|
# Posted: 12 Nov 2016 01:38pm - Edited by: toyota_mdt_tech
Reply
I dont think so, doesnt it need a support box? Frame in a support box and insulate up to that point.
|
|
MtnDon
Member
|
# Posted: 12 Nov 2016 05:24pm - Edited by: MtnDon
Reply
One of the stove pipe rules is that all black pipe should be 18" distant from any combustible. Factory made chimneys always use insulated pipe through a ceiling or wall. My chimney uses a short length (12") of insulated pipe dropped from the ceiling. Along with that a metal collar rings the insulated pipe like a big washer. There is no wood directly above that within the danger zone.
It uses a metal support box as was mentioned. The upper lengths of insulated pipe rest on that.
Anything else is a fire hazard.
|
|
|